TC-32 Alarm Output's


TWorle

Question

Hi

I am considering buying some TC-32's. Is it possible to configure a single digital output to be triggered if any temperature is outside of its limits?

For example, am I able (Using the ULDAQ Linux SDK) to configure channels 0, 3 and 5 with different alarm temperatures. If any of those individual alarms are exceeded then DO1 should go high.

Link to comment
Share on other sites

3 answers to this question

Recommended Posts

  • 0

Programmatically, you can connect to the TC-32 using either USB or Ethernet. Channels can be individually set to a TC type. You can enable open TC detection and TC filtering, either 50 or 60 Hz. You have complete control over the 8-bit digital input port and the two 32-bit output ports. Reading the TC channels can be done one at a time or by group. The only exception to your list is field calibration. That can only be done using a Windows computer and the InstaCal utility. 

Link to comment
Share on other sites

  • 0

Thanks for the confirmation.

Just slightly concerned that some functionality isn't available through the SDK. Am I still able to use most of the core functionality of the device. In my mind that is:

  • Connect to the TC-32
  • Read data from the TC-32
  • Perhaps configure the channel settings (Thermocouple type etc)
  • Perhaps calibration functions
Link to comment
Share on other sites